125% Largest Motor Value follow all the way to the switchboard?

Status
Not open for further replies.

AWinston

Member
Location
Murrieta, Ca
I am working on a facility with a lot of HVAC and a lot of sub panels. I properly show the 125% demand factor for the largest motor on each sub panel. Does that 125% value on each panel follow all the way to the main switchboard? Or am I only supposed to show the 125% largest motor demand factor on the overall largest motor in the facility? We are well over the service size and I'm trying to find every possible solution.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
When you calculate the load on any single branch circuit panel, you count 125% of the largest motor fed from that panel. When you calculate the load on a distribution panel that feeds several downstream branch circuit panels, each of which feeds motors, you count 125% of the one largest motor fed from any of the downstream panels. When you calculate the load on the main switchboard, you count 125% of the one largest motor in the entire building. Does that make sense?
 