greenspark1
Senior Member
- Location
- New England
Hi all. A basic question but one I haven't found clearly answered in the Code. Using 220.84 I calculated 850A load for a new multifamily project. Now to size the service, 230.31 (A) says to use the load calculated in Article 220. Easy, 850A. However, for underground services (which is what this will be), 230.42(A) requires 125% of continuous loads plus 100% of non-continuous. How does this requirement relate to 220.84, which doesn't differentiate between continuous and non-continuous and instead basically provides a blended diversity factor.
Bottom line, is 850A rated conductor/breaker Code minimum, or must I take 125% of 850A, or some other option? I feel that 850A conductors is acceptable.
Bottom line, is 850A rated conductor/breaker Code minimum, or must I take 125% of 850A, or some other option? I feel that 850A conductors is acceptable.