I'm working on a project where we are adding loads to an existing service and am getting some conflicting opinions on whether we need to have a 125% multiplier at the service entrance for new loads we're adding, all of which are considered continuous.
Topology is straight forward: New feeder breaker in the service entrance feeds a step-down transformer that feeds a panel that feeds the loads.
All the branch circuit conductors and feeder circuit conductors are sized for 125% of the load they serve per NEC 210.19(A)(1)(a) and NEC 215.2(A)(1)(a).
The question comes in at the service entrance. Considering NEC 220.87, we have taken the actual demand over a 1-year period, found the maximum demand at 125% plus the new load, and made sure this does not exceed the ampacity of the service entrance. Some of the opinions I have heard is that the new load also needs to be taken at 125% because it is continuous. Others have said that this section doesn't say anything about a multiplier so you take the new load as-is.
I tend to believe that we just take the new load at 100% because the NEC is typically very specific on multipliers or references to other sections of the code that apply in a given situation. But I want to make sure I'm not missing anything here.
Topology is straight forward: New feeder breaker in the service entrance feeds a step-down transformer that feeds a panel that feeds the loads.
All the branch circuit conductors and feeder circuit conductors are sized for 125% of the load they serve per NEC 210.19(A)(1)(a) and NEC 215.2(A)(1)(a).
The question comes in at the service entrance. Considering NEC 220.87, we have taken the actual demand over a 1-year period, found the maximum demand at 125% plus the new load, and made sure this does not exceed the ampacity of the service entrance. Some of the opinions I have heard is that the new load also needs to be taken at 125% because it is continuous. Others have said that this section doesn't say anything about a multiplier so you take the new load as-is.
I tend to believe that we just take the new load at 100% because the NEC is typically very specific on multipliers or references to other sections of the code that apply in a given situation. But I want to make sure I'm not missing anything here.