FaradayFF

Senior Member
Location
California
Hi Guys,

Can you recommend a meter mains product, 125Amp socket with 100Amp breaker, ring type? I looked at offerings by Eaton and Cutler-Hammer, they don't have the above configuration with ring type meter sockets...

Thanks,
EE
 
Some utilities will not accept ringless. Less exposure to the meterman removing the meter because the cover stays on. The downside is, with the cover on, internal damage may not be seen until the arc flash has Happened.
 
For a 125 Amp wattmeter, can I order a 200 Amp meter socket?
Eaton has a 100Amp ring type socket, but I need a higher amperage socket, since my max service Amp is 105 Amp.
 
Hi Guys,

Can you recommend a meter mains product, 125Amp socket with 100Amp breaker, ring type? I looked at offerings by Eaton and Cutler-Hammer, they don't have the above configuration with ring type meter sockets...

Thanks,
EE

I don't believe you, at least initially. They must have that configuration.
 