Looking for guidance from you and NEC that would help validate our position on an installation where we needed to install 30A breakers in a remote controlled power distribution panel utilizing AWG12 wire. With 20A breakers in place, we experienced multiple 'nuisance tripping' when the main panel was energized. The load is an electronic video display, with multiple power supplies, transformers, and LED modules. The tripping is attributed to very brief inrush current. The full load on any single circuit ranges from 8.6A to 11.4A. The service is 277/480 3 phase, and there are 150 circuits in the power panel.
Our nominal and even max loads are well within the load calculations for running on 12AWG wire, but the spike in current at startup in the first 5 or less milliseconds creates the need for the inrush capability of the 30A breaker. In terms of risk, if a short circuit condition were to take place, the spike in amps would still trip a 30A breaker, and in the case of a thermal or overload condition, the power supplies would go into shutdown. So there is little risk with this setup.
Note on Riser diagram "30A circuit breakers installed to account for inrush of power supplies at 277V to avoid nuisance tripping."
This load for our display installation is not a motor, but we liken the situation to motor overcurrent circuit protection. Circuit breakers for motor wiring may be upsized by up to 250% to account for inrush. It is possible to have 12AWG connected to a 60 amp breaker and still be code compliant. We understand the main reason why it is allowable is because motors are required to have thermal overload protection in addition to the circuit overcurrent protection. Similar to power supply wiring, if a short circuit occurs in the motor wiring, the spike in amps will still trip the upsized circuit breaker. And similar to how the power supplies in our display will shut down in the case of a thermal or overload condition, the overload protection on the motor will shut the motor down (not the circuit breaker.
We believe the case for allowing 12AWG with a 30A breaker in this specific situation is made stronger by reviewing conductor ampacities from the tables in NEC from 310.15 (2017 edition). The ampacity of 12 AWG THHN/THWN conductors in free air (which is what they are internal to our electronic display) is 40A.
Other examples of carve outs in the NEC that strengthen the case would be:
· Next higher standard overcurrent protection device rating allowed above the ampacity of the conductors being protected per 240.4 (B)
· A case could be made for using 12 AWG with a 30A breaker according to the Tap rules in 240.21.
· Carve outs for fixture wiring used with listed appliances in 240.5 B is also relevant in terms of safe wiring practices where smaller than typical wiring is allowed to be tapped to a larger circuit breaker than is allowed per 240.4 D 1-7.
· Table 240.4(G) is an entire list of applications where smaller conductors may be permitted.
· 310.15 (C) is another carve out where under engineering supervision conductor ampacities are allowed to be calculated differently.
We would appreciate your insight on how we can more clearly reference the NEC to assure the customer this installation is appropriate and safe. The customer is only thinking that 12AWG wire can connect to 20A breakers - no exceptions. We believe this to be an exception, but are looking to provide additional backup from NEC.
Thank you.
Our nominal and even max loads are well within the load calculations for running on 12AWG wire, but the spike in current at startup in the first 5 or less milliseconds creates the need for the inrush capability of the 30A breaker. In terms of risk, if a short circuit condition were to take place, the spike in amps would still trip a 30A breaker, and in the case of a thermal or overload condition, the power supplies would go into shutdown. So there is little risk with this setup.
Note on Riser diagram "30A circuit breakers installed to account for inrush of power supplies at 277V to avoid nuisance tripping."
This load for our display installation is not a motor, but we liken the situation to motor overcurrent circuit protection. Circuit breakers for motor wiring may be upsized by up to 250% to account for inrush. It is possible to have 12AWG connected to a 60 amp breaker and still be code compliant. We understand the main reason why it is allowable is because motors are required to have thermal overload protection in addition to the circuit overcurrent protection. Similar to power supply wiring, if a short circuit occurs in the motor wiring, the spike in amps will still trip the upsized circuit breaker. And similar to how the power supplies in our display will shut down in the case of a thermal or overload condition, the overload protection on the motor will shut the motor down (not the circuit breaker.
We believe the case for allowing 12AWG with a 30A breaker in this specific situation is made stronger by reviewing conductor ampacities from the tables in NEC from 310.15 (2017 edition). The ampacity of 12 AWG THHN/THWN conductors in free air (which is what they are internal to our electronic display) is 40A.
Other examples of carve outs in the NEC that strengthen the case would be:
· Next higher standard overcurrent protection device rating allowed above the ampacity of the conductors being protected per 240.4 (B)
· A case could be made for using 12 AWG with a 30A breaker according to the Tap rules in 240.21.
· Carve outs for fixture wiring used with listed appliances in 240.5 B is also relevant in terms of safe wiring practices where smaller than typical wiring is allowed to be tapped to a larger circuit breaker than is allowed per 240.4 D 1-7.
· Table 240.4(G) is an entire list of applications where smaller conductors may be permitted.
· 310.15 (C) is another carve out where under engineering supervision conductor ampacities are allowed to be calculated differently.
We would appreciate your insight on how we can more clearly reference the NEC to assure the customer this installation is appropriate and safe. The customer is only thinking that 12AWG wire can connect to 20A breakers - no exceptions. We believe this to be an exception, but are looking to provide additional backup from NEC.
Thank you.