12AWG Wire Terminated to 600A Breakers

Usama

Member
Location
Florida
Occupation
Electrical Engineer
In doing a safety inspection for a building saw a #12AWG Wire terminated to 600A breakers. Any idea what some was thinking when tapping this here? Wasn't able to determine the downstream load, this is a main service disconnect fed from the utility. Also should note this is a large tower where this service disconnect exists every 3 floors and they all have this tap.

 
Possibly in the Utility Tx Room, however, I wasn't able to get access into this room. I tried looking for information on the breaker, to see if it had a shunt trip function, however given the age wasn't able to find anything fruitful. That said, it's an old FP 600A breaker.

Shunt trip makes the most sense as why they used wire nuts and tapped the feed rather than feeding directly into the terminals.
 
Your bigger problem is likely those little FPE breakers, the big breaker will function fine those FPE breakers might just be welded on.
 
In doing a safety inspection for a building saw a #12AWG Wire terminated to 600A breakers. Any idea what some was thinking when tapping this here? Wasn't able to determine the downstream load, this is a main service disconnect fed from the utility. Also should note this is a large tower where this service disconnect exists every 3 floors and they all have this tap.

Can't see your picture anymore. Just a guess, it was common in the good old days to wire in an emergency light to the main breaker.
 
Shut trip would be to terminals on the breaker NOT tapping the feed.
This is a tap:
View attachment 2577087
They are probably tapping the breaker to power the shunt trip. The two small wires out of the bottom of the breaker is the shunt trip coil. Don’t know if FPE has clearing contacts built in, or the EPO switch is momentary contact, but it is better to have the control power off the load side, instead of the line side.
 