Mcooke
- Santa Cruz, CA
- Construction Manager
I'm working on a project and we are about to start a MV tie-in, 15kv copper tape shielded cable. One of the facility electricians is saying that the MV Feeds both A/B originating from an existing vault need an equipment grounding conductor run in the conduit with the MV Cable. The MV Feeds consist of 3, 4/0 cables, no grounded conductor. The duct bank has one bare #2 copper grounding electrode (could be EGC in this case?) in it that will be bonded to the grounding ring/switch rack and enclosure at the new vacuum disconnect switch and to the grounding configuration (ground rod) at the existing vault.
Does the utility side of system like this typically require a equipment grounding conductor with each feed A/B of the MV Cables? The drawings do not indicate a ground as one would typically expect to see it occuring on the secondary side of the TX rather than primary.
Thanks in advance!
Thanks in advance!