JFletcher
Senior Member
- Location
- Williamsburg, VA
Are there any code sections other than 680.22(C)* that deal with 12V landscaping light distances from the inside of the pool wall? 3W Led lights are to be installed 8' from water's edge. Mfg directions list 10' minimum; is this distance on the 11 or 14 code cycle, international codes, or just a number they pulled from the air? The 300W transformer is cord and plug and fed from a GFCI receptacle in the crawlspace.
*411.4(B) in the 08 NEC lists 10', unless permitted by article 680. Does that read they same way in the 2011/14 books? 680.22(C)(4) permits an 8' install if the luminaires are GFCI protected, yes? Does the fact that there is an xfmr in the mix change anything?
Yes, I know, 110.3(B), but I'd change mfg if possible rather than push the lights 2' off of the concrete deck in the middle of the grass, illuminating nothing.
eta: these are not cord and plug; they are DC and use IDC connectors on 2 conductor stranded DB cable.... does that make it an "other outlet" as defined in 680.22(E)?
*411.4(B) in the 08 NEC lists 10', unless permitted by article 680. Does that read they same way in the 2011/14 books? 680.22(C)(4) permits an 8' install if the luminaires are GFCI protected, yes? Does the fact that there is an xfmr in the mix change anything?
Yes, I know, 110.3(B), but I'd change mfg if possible rather than push the lights 2' off of the concrete deck in the middle of the grass, illuminating nothing.
eta: these are not cord and plug; they are DC and use IDC connectors on 2 conductor stranded DB cable.... does that make it an "other outlet" as defined in 680.22(E)?
Last edited: