What is considered to be an acceptable voltage drop in a far master bedroom?
I take the code voltage drop FPN as guidance but I think it can be achieved using a mean average voltage drop calculation.
However in tract homes this means you have much higher VD at the end of the run. What is a good maximum for far receptacles say the last in the chain?
I am in the process testing and repairing a new home that was repossessed then auctioned off.
It was wired with one 15A AFCI bedroom circuit. Here in Oregon AFCI is only required in bedrooms still so contractors use as few breakers as possible. Looking at the way the circuit was run around each bedroom, then around a bathroom supplying 2 vent fans several cans, 2 light bars, a hall way with a few cans, 2 outdoor GFCI's (another story) ...etc I would not be surprised if it was 200 - 275' in length of 14AWG wire.
Testing the 15A AFCI circuit with an Ideal Suretest reveals a 13 - 14 % voltage drop at a 12A load 120V at every receptacle in the master bedroom.
I checked for loose connections etc. All receptacles, devices had been removed in haste by former owner whom got foreclosed on and the wires cut short in the boxes, all the wires were pigtailed by us. VD gets lower and more normal the closer I get to the panel so I am eliminating the possibility of a bad splice.
I double checked the splices and they look good.
Doing a quick calculation:
15.0 Amps Rated ampacity.
2.9495 Ohms Resistance (Ohms per 1000 feet)
0.058 Ohms Reactance (Ohms per 1000 feet)
16.8 volts voltage drop at 14%
0.9 Power Factor
Gives me 261.21 Feet.
So my 14% drop would be expected for that much 14/2.
I am considering pulling a 12AWG to a place on the circuit where I can split it in two and putting the bedroom on its own 15A AFCI.
Over kill?
Thanks in advance!
I take the code voltage drop FPN as guidance but I think it can be achieved using a mean average voltage drop calculation.
However in tract homes this means you have much higher VD at the end of the run. What is a good maximum for far receptacles say the last in the chain?
I am in the process testing and repairing a new home that was repossessed then auctioned off.
It was wired with one 15A AFCI bedroom circuit. Here in Oregon AFCI is only required in bedrooms still so contractors use as few breakers as possible. Looking at the way the circuit was run around each bedroom, then around a bathroom supplying 2 vent fans several cans, 2 light bars, a hall way with a few cans, 2 outdoor GFCI's (another story) ...etc I would not be surprised if it was 200 - 275' in length of 14AWG wire.
Testing the 15A AFCI circuit with an Ideal Suretest reveals a 13 - 14 % voltage drop at a 12A load 120V at every receptacle in the master bedroom.
I checked for loose connections etc. All receptacles, devices had been removed in haste by former owner whom got foreclosed on and the wires cut short in the boxes, all the wires were pigtailed by us. VD gets lower and more normal the closer I get to the panel so I am eliminating the possibility of a bad splice.
I double checked the splices and they look good.
Doing a quick calculation:
15.0 Amps Rated ampacity.
2.9495 Ohms Resistance (Ohms per 1000 feet)
0.058 Ohms Reactance (Ohms per 1000 feet)
16.8 volts voltage drop at 14%
0.9 Power Factor
Gives me 261.21 Feet.
So my 14% drop would be expected for that much 14/2.
I am considering pulling a 12AWG to a place on the circuit where I can split it in two and putting the bedroom on its own 15A AFCI.
Over kill?
Thanks in advance!