This is a question that was posted on another forum. I would appreciate any comments to my response:
"We are installing a 13KV to 480/277 volt 1000kva 3phase transformer for an MCC in an idustrial facility. We are using 3 Paralleled 500mcm per phase (1200amp secondary). Where do you size the ground for this installation? For this size conductor Table 250-66 calls for a 3/0 grounding electrode conductor. It will be protected on the primary side for the secondary conductors. Table 250-122 list 3/0 for a 1200amp overcurrent protection device, if this applies since it doesn't actually have a 1200amp protective device.
First question: Which table would you use to size the ground for the secondary?
Second question: If it is 3/0 which seems to be indicated, can you parallel 2 2/0 instead of the 3/0?
Response
The post seems to indicate that the primary 13kv and the transformer are customer owned. If so, then the 13kv is the service and I assume there is a primary disconnect switch at the site some where. The conductors secondary, 3 500 kcm per phase, are then feeder conductors. Since 3 # 500 75C conductors are rated at 380 x 3 = 1140 amps, there is a violation of 240.3.C. The secondary needs to be 3 # 600 kcm or equal to match the 1200 amp main. 240.21C(1) thru C(6) also comes into play. The length of the conductors was not listed but the requirements of C2, C3, C4 where applicable. All of these require that the conductors be rated at 1200 amps.
The quote "It will be protected on the primary side for the secondary conductors. Table 250-122 list 3/0 for a 1200amp overcurrent protection device, if this applies since it doesn't actually have a 1200amp protective device." The main OC protection is the transformer primary fuse as stated. If you assume that the transformer fuse is 200% of the FLA as allowed by table 450.3A then (1000 kva)/(1.73x 13.2) = 88 amps or a 90 amps fuse or 2055 kva. Relating this to the secondary you have 2055 kva/(.48 x 1.73) = 2475 amps. According to table 250.122 the EGC is 350 kcm. In addition, this conductor must be able to withstand the fault current imposed on it. Assuming the transformer has 5% impedance, the available fault current is about 24000 amps using infinite buss. The time current curves of the primary fuse will determine the the conductor withstand rating.
Edited to show secondary voltage 277/480 volts
[ September 27, 2004, 01:49 PM: Message edited by: bob ]
"We are installing a 13KV to 480/277 volt 1000kva 3phase transformer for an MCC in an idustrial facility. We are using 3 Paralleled 500mcm per phase (1200amp secondary). Where do you size the ground for this installation? For this size conductor Table 250-66 calls for a 3/0 grounding electrode conductor. It will be protected on the primary side for the secondary conductors. Table 250-122 list 3/0 for a 1200amp overcurrent protection device, if this applies since it doesn't actually have a 1200amp protective device.
First question: Which table would you use to size the ground for the secondary?
Second question: If it is 3/0 which seems to be indicated, can you parallel 2 2/0 instead of the 3/0?
Response
The post seems to indicate that the primary 13kv and the transformer are customer owned. If so, then the 13kv is the service and I assume there is a primary disconnect switch at the site some where. The conductors secondary, 3 500 kcm per phase, are then feeder conductors. Since 3 # 500 75C conductors are rated at 380 x 3 = 1140 amps, there is a violation of 240.3.C. The secondary needs to be 3 # 600 kcm or equal to match the 1200 amp main. 240.21C(1) thru C(6) also comes into play. The length of the conductors was not listed but the requirements of C2, C3, C4 where applicable. All of these require that the conductors be rated at 1200 amps.
The quote "It will be protected on the primary side for the secondary conductors. Table 250-122 list 3/0 for a 1200amp overcurrent protection device, if this applies since it doesn't actually have a 1200amp protective device." The main OC protection is the transformer primary fuse as stated. If you assume that the transformer fuse is 200% of the FLA as allowed by table 450.3A then (1000 kva)/(1.73x 13.2) = 88 amps or a 90 amps fuse or 2055 kva. Relating this to the secondary you have 2055 kva/(.48 x 1.73) = 2475 amps. According to table 250.122 the EGC is 350 kcm. In addition, this conductor must be able to withstand the fault current imposed on it. Assuming the transformer has 5% impedance, the available fault current is about 24000 amps using infinite buss. The time current curves of the primary fuse will determine the the conductor withstand rating.
Edited to show secondary voltage 277/480 volts