Let me start by saying I love this forum. I'm new ... be gentle.
The code inspector on our project stated 110.34 as the reason for requiring 5 feet of clearance in front of the sub-station (13.2kV primary switch feeding 300kVA 13.2kV to 208V xfmr and 800A panel).
When I read 110.34 it states ?equipment likely to require examination, adjustment, servicing, or maintenance while energized shall have??. The EC said they would never open that enclosure while energized, and there is an upstream switch, so to me those distances do not apply and we revert back to 110.26, condition 2, which requires 3 feet.
Our EE is traveling but confirmed 5 feet is required but did not reference which code section required it. Is 5 feet just the accepted industry standard or do I need to be referencing another section.
Thanks.
The code inspector on our project stated 110.34 as the reason for requiring 5 feet of clearance in front of the sub-station (13.2kV primary switch feeding 300kVA 13.2kV to 208V xfmr and 800A panel).
When I read 110.34 it states ?equipment likely to require examination, adjustment, servicing, or maintenance while energized shall have??. The EC said they would never open that enclosure while energized, and there is an upstream switch, so to me those distances do not apply and we revert back to 110.26, condition 2, which requires 3 feet.