Hey All,
I have been a long-time reader and user of this forum but have never posted anything. I appreciate any information and feedback that you provide.
Summary:
I am designing an industrial power system for multiple 13.8 kV generators to run in parallel. The grounding scheme currently in place at other locations (not by my design) does not have the equipment ground tied through to the switchgear and downstream loads. The generators have individual ground grids that are bonded together (3 ground rods in a triangle each) and then the switchgear and loads have individual ground grids (same ground rod configuration). The generation GEC and the switchgear GEC are not tied together. That means that any ground fault that occurs would be returning through the earth back to the generators.
Here are some of the high-level details:
- The generators have 13.8kV Wye output and each has a separate high-resistance ground.
- The cable assembly from the generator to the switchgear is a 3-wire, 15kV heavy-duty portable power cable WITHOUT a ground terminated.
- The cable assembly from the switchgear to the loads is a 3-wire, 15kV heavy-duty portable power cable WITH ground terminated.
- The loads each have separate low-resistance grounds.
- Here is the link to a simple drawing that I have made: https://ibb.co/PvV1RhWg
My thoughts:
The big problem that I see here is the path back to the source is unknown and therefore the resistance in the path through earth is unknown. This could affect the generator relay ground pickup elements since we could be adding resistance in the path back to the source. I strongly believe that the switchgear GE's should be tied back to the generation GE's. NEC 250.4(A)(5) clearly states that the earth shall not be considered an effective ground-fault return path, and NEC 250.54 allows auxiliary GE's but references 250.4(A)(5), so I take that as they need to be bonded to the GEC. From a safety perspective, I cannot definitively say this is unsafe since I do not know if the step/touch potential exceeds 50VAC, but I would not be surprised if there was a difference in potential. Mike Holt had a great article that I found in research that talks about how ground rods do not reduce touch potential here.
My questions I have:
I would like to know if anyone has seen something similar to this and can point to other standards that would allow the isolation of the GE's. I have looked through the NEC, IEEE-142, and IEEE-80 and have yet to find an exception to this. Regarding safety, I would like to know your thoughts and experience in situations like this. On the auxiliary grounding for the switchgear and loads, I have not done a lot of multi-grounded schemes before, but I do not see a risk here and would like to know your thoughts on keeping/removing those and making it a single-point grounded system. Again, I believe that the grounding from generation to switchgear is incorrect and should be addressed but would like to use the knowledge base of this forum to shoot holes in my analysis lol.
I have been a long-time reader and user of this forum but have never posted anything. I appreciate any information and feedback that you provide.
Summary:
I am designing an industrial power system for multiple 13.8 kV generators to run in parallel. The grounding scheme currently in place at other locations (not by my design) does not have the equipment ground tied through to the switchgear and downstream loads. The generators have individual ground grids that are bonded together (3 ground rods in a triangle each) and then the switchgear and loads have individual ground grids (same ground rod configuration). The generation GEC and the switchgear GEC are not tied together. That means that any ground fault that occurs would be returning through the earth back to the generators.
Here are some of the high-level details:
- The generators have 13.8kV Wye output and each has a separate high-resistance ground.
- The cable assembly from the generator to the switchgear is a 3-wire, 15kV heavy-duty portable power cable WITHOUT a ground terminated.
- The cable assembly from the switchgear to the loads is a 3-wire, 15kV heavy-duty portable power cable WITH ground terminated.
- The loads each have separate low-resistance grounds.
- Here is the link to a simple drawing that I have made: https://ibb.co/PvV1RhWg
My thoughts:
The big problem that I see here is the path back to the source is unknown and therefore the resistance in the path through earth is unknown. This could affect the generator relay ground pickup elements since we could be adding resistance in the path back to the source. I strongly believe that the switchgear GE's should be tied back to the generation GE's. NEC 250.4(A)(5) clearly states that the earth shall not be considered an effective ground-fault return path, and NEC 250.54 allows auxiliary GE's but references 250.4(A)(5), so I take that as they need to be bonded to the GEC. From a safety perspective, I cannot definitively say this is unsafe since I do not know if the step/touch potential exceeds 50VAC, but I would not be surprised if there was a difference in potential. Mike Holt had a great article that I found in research that talks about how ground rods do not reduce touch potential here.
My questions I have:
I would like to know if anyone has seen something similar to this and can point to other standards that would allow the isolation of the GE's. I have looked through the NEC, IEEE-142, and IEEE-80 and have yet to find an exception to this. Regarding safety, I would like to know your thoughts and experience in situations like this. On the auxiliary grounding for the switchgear and loads, I have not done a lot of multi-grounded schemes before, but I do not see a risk here and would like to know your thoughts on keeping/removing those and making it a single-point grounded system. Again, I believe that the grounding from generation to switchgear is incorrect and should be addressed but would like to use the knowledge base of this forum to shoot holes in my analysis lol.