Hello,
I have an application where I am designing a feeder rated for 4.0MW (197 amps) at 13.8kV from an existing switchgear.
The cubicle that I am utilizing is a 1200 amp fully equipped space for which I have specified a 15kV, 1200 amp breaker and SEL-351 relay.
NEC 215.3.B seems unclear to me about how to size the cables. For 13.8kV (medium voltage) the cables can be sized for load only, correct?
I was originally going to use a 3/C - 2/0 with ground cable, but I am looking on the existing one-line and all the feeders are 3 - 500kCMIL or 6 - 500kCMIL.