F frostback Member May 11, 2004 #1 WHAT IS THE CORRECT SIZE 13.8KV CABLE FOR THE PRIMARY SIDE OF A 1500KVA XFMR/277/480V SECONDARY
B bennie Esteemed Member May 11, 2004 #2 Re: 13.8KV SWITCH AND 1500 KVA XFMR Depends on the calculated load.
F frostback Member May 11, 2004 #3 Re: 13.8KV SWITCH AND 1500 KVA XFMR LETS SAY THE CONNECTED LOAD IS 1300 KVA THE FEEDER IS OVERHEAD IN A PARKING RAMP,HEATED, IN A 4" RIGID STEEL CONDUIT
Re: 13.8KV SWITCH AND 1500 KVA XFMR LETS SAY THE CONNECTED LOAD IS 1300 KVA THE FEEDER IS OVERHEAD IN A PARKING RAMP,HEATED, IN A 4" RIGID STEEL CONDUIT
T tkirk911 Member May 11, 2004 #4 Re: 13.8KV SWITCH AND 1500 KVA XFMR Primary is approximately 54 amps but here in Delaware we always pull 1/0 for primary. I think it is an Electric Company policy.
Re: 13.8KV SWITCH AND 1500 KVA XFMR Primary is approximately 54 amps but here in Delaware we always pull 1/0 for primary. I think it is an Electric Company policy.
ron Senior Member Location New York, 40.7514,-73.9925 May 11, 2004 #5 Re: 13.8KV SWITCH AND 1500 KVA XFMR You'll find at the ampacity that you need, the smallest 15kV cable made will be larger than you need. I think the smallest is 1/0AWG. http://www.okonite.com/Product_Catalog/section2/sheet8.html [ May 11, 2004, 07:13 PM: Message edited by: ron ]
Re: 13.8KV SWITCH AND 1500 KVA XFMR You'll find at the ampacity that you need, the smallest 15kV cable made will be larger than you need. I think the smallest is 1/0AWG. http://www.okonite.com/Product_Catalog/section2/sheet8.html [ May 11, 2004, 07:13 PM: Message edited by: ron ]