13.8KV SWITCH AND 1500 KVA XFMR

Status
Not open for further replies.
Re: 13.8KV SWITCH AND 1500 KVA XFMR

LETS SAY THE CONNECTED LOAD IS 1300 KVA
THE FEEDER IS OVERHEAD IN A PARKING RAMP,HEATED,
IN A 4" RIGID STEEL CONDUIT
 
Re: 13.8KV SWITCH AND 1500 KVA XFMR

Primary is approximately 54 amps but here in Delaware we always pull 1/0 for primary. I think it is an Electric Company policy.
 