Our plant has an overhead 13.8kv distribution system (open air 3 phases and a static line - much like utility company; but, all owned and maintained by the plant). My question is that when a pole mounted outdoor transformer is installed to supply a buidling does it meet code to bond the transformers X0 (neutral) to the static line, a locally driven ground rod at base of pole, the neutral conductor feeding the building, and a ground conductor run in the same underground feed to the building. At the building's panel (an exterior service entrance rated panel like a residence) the neutral and ground bus are not bonded to prevent parallel current. Terminated at the building are the two hots, the neutral and the grounding conductor; additionally, a ground rod is driven at the buildling's panel and this is connected to the ground bus only. I know this would be ok for a seperately derived system just confused on the fact that the neutral to the transformer is bonded to the primary's static line (so not seperately derived right?) and the code requirements to have an additionally electrode for outdoor transformer. If this installation did not have the grounding conductor then I would drive the rod at the transformer and bond to the neutral (grounded conductor) and then another rod at the panel with that connected to the panel neutral and then have a main bonding jumper; but, since there is a grounding conductor with the two hots and neutral from the pole transformer the netural and ground should remain unbonded except at the transfomer - right?