13.8kV transformer working clearances

Status
Not open for further replies.

Dale001289

Senior Member
Location
Georgia
Do the working clearances shown in NEC 110 apply to oil fill power transformers?
Client has installed a chain link fence approximately 3 feet from the 13.8kV primary side of a 3MVA power transformer. The primary has two doors that can be opened manually however it does have locking capability -
This seems too close to me
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Do the working clearances shown in NEC 110 apply to oil fill power transformers?
Client has installed a chain link fence approximately 3 feet from the 13.8kV primary side of a 3MVA power transformer. The primary has two doors that can be opened manually however it does have locking capability -
This seems too close to me

5’ min per NFPA 70E


Sent from my iPhone using Tapatalk
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Fencing around enclosed equipment, like padmount transformers, is different than what is required for open air equipment.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Fencing around enclosed equipment, like padmount transformers, is different than what is required for open air equipment.

In other words the 10’ distance only applies to open air connections such as an outdoor ‘utility’ type substation transformer?


Sent from my iPhone using Tapatalk
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The fence represents a condition 2.
So why is the distance XFMR to fence twice the amount as the working clearance?
Doesn’t seem to make sense to me.


Sent from my iPhone using Tapatalk
The code text above Table 110.31 says that that table applies to other than equipment described in 110.31(D). The equipment described in that first level subdivision is all enclosed equipment. It appears that the transformer in this thread is enclosed equipment.
 

busman

Senior Member
Location
Northern Virginia
Occupation
Master Electrician / Electrical Engineer
Would the shotgun stick be needed for the enclosed 13.8kV primary side XFMR ?


Sent from my iPhone using Tapatalk
Maybe it's just me, but I wouldn't pull ANY energized MV elbow directly with my hands, even gloved. Also, if the elbow is difficult, you may need an impact elbow puller which are usually about 6' long.