malachi constant
Senior Member
- Location
- Minneapolis
I was under the impression a 13kV 1000kVA transformer, when installed indoors, needs to be in a 3-hr rated vault. Looking at the code I see 450.21(B) requires xfmrs rated over 112.5kVA to be in a 1hr rated room, and 450.21(C) requires (by referencing Part III and 450.42) that transformers rated over 35KV be in a 3-hr rated vault.
So am I correct that the 13kV, 1000kVA transformer, installed indoors, needs a 1-hr rating - not a 3-hr rating?
So am I correct that the 13kV, 1000kVA transformer, installed indoors, needs a 1-hr rating - not a 3-hr rating?