14-2 and 12-2 spliced together

Status
Not open for further replies.
I trimmed a house today and the guys who ran the central vac put a 12-2 NB in a outlet that we had next to the vac hook up (14-2). They created box fill on some boxes that we had to fix. Something seems wrong. Could someone refrence a code so I can study up on this. Thanks
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
monkey_man_100 said:
I trimmed a house today and the guys who ran the central vac put a 12-2 NB in a outlet that we had next to the vac hook up (14-2). They created box fill on some boxes that we had to fix. Something seems wrong. Could someone refrence a code so I can study up on this. Thanks


What specifically are you looking for. Do you want box fill info, etc?
 

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
monkey_man_100 said:
...the central vac put a 12-2 NB in a outlet that we had next to the vac hook up (14-2)....

Are you questioning the 12/2 to 14/2 connection? If the circuit was run in 14 and the OCPD is sized for the 14, 15 amp, then you can up size the conductors, 12. You just cannot go the other way.
 