Assuming that this topic had been previously addresses, I searched through out the site and could not find the answer.
The circuit runs from a 20A breaker in the lighting panel, through EMT to a 4? sq box (#12 THHN), drops out of the box wt #12 MC, down a cable tray and into a 4? sq box and converts back to #12 THHN. The # 12 THHN is distributed via ? EMT to 4? sq boxes located within 3? of each fixture.
Question one: If I install one 6? whip for each lighting fixture from a 4? square box located approx 3? from the fixture, can I use #14 THHN from the fixture to the box?
Second Question: The branch circuit feeding the above mentioned light is a #12 MC cable installed in a 36? Cable Tray mounted above a drop ceiling. The cables are installed tight against one another and secured with wire ties. They are not bundled together or stacked on top of each other. Do I need to derate the wires within this cable tray?
The circuit runs from a 20A breaker in the lighting panel, through EMT to a 4? sq box (#12 THHN), drops out of the box wt #12 MC, down a cable tray and into a 4? sq box and converts back to #12 THHN. The # 12 THHN is distributed via ? EMT to 4? sq boxes located within 3? of each fixture.
Question one: If I install one 6? whip for each lighting fixture from a 4? square box located approx 3? from the fixture, can I use #14 THHN from the fixture to the box?
Second Question: The branch circuit feeding the above mentioned light is a #12 MC cable installed in a 36? Cable Tray mounted above a drop ceiling. The cables are installed tight against one another and secured with wire ties. They are not bundled together or stacked on top of each other. Do I need to derate the wires within this cable tray?