14 gauge wire on 30 amp DP breaker

Status
Not open for further replies.

slick 50

Senior Member
A question popped up about landing the wires of a whole house surge protector under a 30 amp DP breaker. The surge manufacturer recommends that you keep the conductors as short as possible. Is there anything in the NEC stating that within the panel you have to follow that rule. Since the conductors are all inside the panel and there really is no load drawn by the surge protector, can you land under the closest 2 pole breaker even if it is a 2 pole 50. I do understand that the conductors coming off of the surge are 14 gauge. Is there somekind of tap rule or "????

THX:confused:
 

masterinbama

Senior Member
Is the surge protector UL listed? If it is, follow the instructions provided and let er rip.Ive installed some 3 phase models that called for a 100 amp 3 pole. But the unit only had #10 leads.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Also keep in mind that if you are connecting to an existing breaker with another load that the breaker must be listed for multiple wires if you are going to land more than one wire in the breaker terminal.

Chris
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Since the conductors are all inside the panel and there really is no load drawn by the surge protector, can you land under the closest 2 pole breaker even if it is a 2 pole 50.
Unless you mean a breaker rated for only one wire per terminal, then yes.

The shortest-path requirement is for best performance of the surge protector.
 