14 gauge wire on outlet circuits, still OK?

Status
Not open for further replies.

brycenesbitt

Senior Member
Location
United States
I had someone I normally trust on NEC/Code issues say that all outlet branches must use 12 gauge/20 amp wire
and that 14 gauge wire was only for lighting circuits now. True that? If so could I get a reference?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
NYC local code amendment has #12 AWG as the minimum branch circuit conductor size. This is not in the NEC.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I had someone I normally trust on NEC/Code issues say that all outlet branches must use 12 gauge/20 amp wire
and that 14 gauge wire was only for lighting circuits now. True that? If so could I get a reference?
Ask the person who told you this to give you a reference.

Roger
 
Status
Not open for further replies.
Top