Paul the BIG Finn
Member
- Location
- Ashburn, VA
The project adds additional air conditioning in a relatively small commercial building. The size of the required air conditioning units requires 3-phase power and an increase in service size from 400A, 120/240V, 1PH, 3W to 600A 120/208V, 3PH, 4W. The utility informs us the new available fault current is 14 kAIC, while the original panelboards are rated 10 kAIC. Not wanting to incur the expense and time required to replace 5 panelboards we are looking for methods to reduce the available fault current.
The only solution I can find is a 75 kVA, 208V-120Y/208V transformer to feed a new distribution panel supplying the existing panelboards with 120/208V, 1PH, 3W power. We plan to connect the first panel AB, the 2nd BC and third CA to balance the load. Is there a better solution available?
There is one other problem. There is a small 120/240V emergency generator supplying a 60A, 120/240V, 1PH, 3W paneboard through an ATS. There are no 240V emergency power loads. If we lower the low voltage start to below 198V will there be a problem supplying the utility side of the ATS with 120/208V, 1PH, 3W power?
I'd appreciate any thoughts.
The only solution I can find is a 75 kVA, 208V-120Y/208V transformer to feed a new distribution panel supplying the existing panelboards with 120/208V, 1PH, 3W power. We plan to connect the first panel AB, the 2nd BC and third CA to balance the load. Is there a better solution available?
There is one other problem. There is a small 120/240V emergency generator supplying a 60A, 120/240V, 1PH, 3W paneboard through an ATS. There are no 240V emergency power loads. If we lower the low voltage start to below 198V will there be a problem supplying the utility side of the ATS with 120/208V, 1PH, 3W power?
I'd appreciate any thoughts.