Hello
Considering HV switchgear rated for 145 kV 3 phase 50 Hz. All 3 phase busbars are in one enclosure so 3 phase or 2 phase faults are possible.
Assuming system failure (leakage) and SF6 pressure drop below 2 stage alarm level in feeder
compartment, does the electrical strength of the system still maintained?
I mean that typical distance for HV 3 phase air insulated busbars rated for 145 kV is around 1.1m (3.6 ft.).
In GIS switchgear for space saving issues busbars are closer each other, but in SF6 gas environment which has stronger electrical strength.
In normal condition pressure of SF6 gas in feeder compartment is around 0,6 MPa (87 PSI), but when pressure of SF6 drops severely
how to maintain electrical strength of the compartment. Compartment has own SF6 pressure loss detector which alarms remote control center, but HV voltage
at cable feeder is still present. Is sparkover between busbars serious threat in such conditions?
Greets
Considering HV switchgear rated for 145 kV 3 phase 50 Hz. All 3 phase busbars are in one enclosure so 3 phase or 2 phase faults are possible.
Assuming system failure (leakage) and SF6 pressure drop below 2 stage alarm level in feeder
compartment, does the electrical strength of the system still maintained?
I mean that typical distance for HV 3 phase air insulated busbars rated for 145 kV is around 1.1m (3.6 ft.).
In GIS switchgear for space saving issues busbars are closer each other, but in SF6 gas environment which has stronger electrical strength.
In normal condition pressure of SF6 gas in feeder compartment is around 0,6 MPa (87 PSI), but when pressure of SF6 drops severely
how to maintain electrical strength of the compartment. Compartment has own SF6 pressure loss detector which alarms remote control center, but HV voltage
at cable feeder is still present. Is sparkover between busbars serious threat in such conditions?
Greets