it wont be how many Switches can be on a circuit. its how many lights and the watts that the lights use. what is the max you use on a circuit? 85% right?
you got the timing down huh. wow.
why only that long
you got the timing down huh. wow.
why only that long
Continuous Load.
A load where the maximum current is expected to continue for 3 hours or more.
sooo. i grabbed my code book and scanned through article 100. all 7 1/2 pages. didnt see anything under continuous loads that amounted to 179 m and however many seconds. howd you come up with the number
even dont see anything in 210.19
No, you can load a circuit to 100% for up to 179 minutes 59 seconds.
It would be 80% for continuous loading.
Roger
and in the definition of continuous load it says nothing about a time limit running a circuit at 100%( 20amps out of 20amps)
No, you can load a circuit to 100% for up to 179 minutes 59 seconds.
It would be 80% for continuous loading.
Roger
Take THAT you 15-amperes.In residential some bosses are cheap and like to run 15 amp circuits to rooms to cover lighting and recepts. I like to run 15 amp lighting only circuits and 20 amp recept only circuits. Thats so when you plug your vac in the lights dont even dim.
Because that's the way the code is writtendont understand why you said it like that.
No it won't change the load but it does change it to a continuous Load.1 more second wont make your load jump to 125%.
Now we're getting on the same page. :wink:and if you count out your circuit to 100% with a countinuous load. 125% rule should be accounted for.
Not saying that is not good practice but, many rules of thumb and myths dye hard sometimesi was just stating that i was taught to only count my circuits to 85% with everything applicable accounted for.
If you have a fully loaded circuit and plug a vacuum in it better trip and that has nothing to do with being continuous or non continuous.Thats so when your pulling a full load on the circuit and you plug in a vaccum you dont trip a breaker.
I don't think it is being cheap if a 15 amp circuit is all that is needed, some people are happy with a Kia and that is all they need while others want CadillacsIn residential some bosses are cheap and like to run 15 amp circuits to rooms to cover lighting and recepts. I like to run 15 amp lighting only circuits and 20 amp recept only circuits. Thats so when you plug your vac in the lights dont even dim.
Agreed.so back to the original question. its not how many switches and boxes you can put on the circuit. its the wattage that the lights and devices use that have to be accounted for
its the wattage that the lights and devices use that have to be accounted for
That's the one thing you've said that I agree with. :smile:I like to run 15 amp lighting only circuits and 20 amp recept only circuits. Thats so when you plug your vac in the lights dont even dim.