15 A Duplex Surge Receptacle On 20 A Circuit

Status
Not open for further replies.

yesterlectric

Senior Member
Location
PA
Occupation
Electrician
Does a 15 amp surge receptacle have to be on a 15 amp breaker or can one install it according to the same 210.23 and 210.24 rules which would allow a duplex or multi receptacle string to have 15 amp receptacles on a 20 amp breaker?
 
What context is the question. Device, or NEC words?

Almost all the Leviton 15A duplex gfi-afi recepts say "15A, 20A feed-through". Beyond that, I don't see install sheets that say "install on 15A ocpd ckt only".

15 Amp, 125 Volt Receptacle/Outlet, 20 Amp Feed-Through, Tamper-Resistant, AFCI Receptacle/Outlet,
 
What context is the question. Device, or NEC words?

Almost all the Leviton 15A duplex gfi-afi recepts say "15A, 20A feed-through". Beyond that, I don't see install sheets that say "install on 15A ocpd ckt only".
Which question? The one regarding whether it's a duplex or a single receptacle? A 15 amp single receptacle is not permitted on a 20 amp circuit.
 
Which question? The one regarding whether it's a duplex or a single receptacle? A 15 amp single receptacle is not permitted on a 20 amp circuit.
The OP's question.
I did reference gfi-afi, OP did say surge.
If it's just a question of if the device itself is ok on a 20A BC, yes, the device is a-ok.

5280-W Leviton surge duplex, is just a duplex, won't feed/protect downstream. Nothing in the install sheets that say "15A ckt only". So, only the std NEC rules apply.
 
The OP's question.
I did reference gfi-afi, OP did say surge.
If it's just a question of if the device itself is ok on a 20A BC, yes, the device is a-ok.

5280-W Leviton surge duplex, is just a duplex, won't feed/protect downstream. Nothing in the install sheets that say "15A ckt only". So, only the std NEC rules apply.
Sure it will it clamps the voltage at the point it is installed so that surge will not appear on the down stream devices unless the surge originates down stream of the surge device.
 
Why would it just clamp downstream (and not upstream) if it's not just the local recept itself. I don't think those surge recepts have "line" "load" terminals. I do not believe the passive components are in series with downstream, unless the surge is like gfi with "line" "load" connections.

original.png
 
The Leviton surge I mentioned, spec sheet states it protects to full rated amps. I take that to mean the inline passive components can handle 15Amax. What if the surge recept had 6A on it, and four downstreams each had 3A on them. 18A would exceed the surge recept max, OCPD still happy.
 
A 15 amp duplex receptacle allows for 15 amps per receptacle (two on the yoke). That's 30 amps...so yeah, putting one on a 20 amp circuit is fine.

Even if there's only one receptacle, you can only plug in a 15A appliance/tool into it. If you overload the circuit, the circuit breaker should trip. The receptacle limits what you can plug in to it. The wiring and circuit breaker limit how many amps you can send through them.
 
Which question? The one regarding whether it's a duplex or a single receptacle? A 15 amp single receptacle is not permitted on a 20 amp circuit.
A 15 amp single receptacle is not permitted to be the only outlet on a 20 amp circuit.

You can have a 20 amp circuit with multiple single 15 amp receptacles.
 
Why would it just clamp downstream (and not upstream) if it's not just the local recept itself. I don't think those surge recepts have "line" "load" terminals. I do not believe the passive components are in series with downstream, unless the surge is like gfi with "line" "load" connections.
...
How would it clamp it before it sees it? It can't do anything before the spike or surge gets to the device, and it is not a time machine so everything on the line side of the device has already seen the spike or surge. The device eliminates or reduces the spike or surge and it no longer exists for the downstream equipment to see.
 
How would it clamp it before it sees it? It can't do anything before the spike or surge gets to the device, and it is not a time machine so everything on the line side of the device has already seen the spike or surge. The device eliminates or reduces the spike or surge and it no longer exists for the downstream equipment to see.
The surge recepts don't have "line" "load" terminals. The compoenents inside are inline with the receptacle. For the same reason when you plug in a surge strip, plugging it in does not protect anything but that strip.
 
A 15 amp duplex receptacle allows for 15 amps per receptacle (two on the yoke). That's 30 amps...so yeah, putting one on a 20 amp circuit is fine.

Even if there's only one receptacle, you can only plug in a 15A appliance/tool into it. If you overload the circuit, the circuit breaker should trip. The receptacle limits what you can plug in to it. The wiring and circuit breaker limit how many amps you can send through them.
Std recepts, but recepts with other components inside may not be able to do any more than rated. Surge recepts have inline components. Although I suspect a 15A rated surge recept can handle 20A, the internals are rated 15A. For that reason I don't think a 15A rated surge recept should be on a 20A BC.

It's a question for say Leviton to explain further their surge recepts, and it's something for the NEC folks to out on an agenda.
 
Last edited:
The surge recepts don't have "line" "load" terminals. The compoenents inside are inline with the receptacle. For the same reason when you plug in a surge strip, plugging it in does not protect anything but that strip.
Is it "in line" or is it just across the conductors kind of same way a whole house protector is, this just happens to be much closer to the point of use than a whole house protector is. If it is just across the conductors then a 2 gang box with one surge receptacle and normal receptacle in it would both have very similar protection simply because of close proximity where in situations where you had down stream receptacles with more distance between there might still be some protection but maybe not as near the same level of protection because of the distance between them.
 
Is it "in line" or is it just across the conductors kind of same way a whole house protector is, this just happens to be much closer to the point of use than a whole house protector is. If it is just across the conductors then a 2 gang box with one surge receptacle and normal receptacle in it would both have very similar protection simply because of close proximity where in situations where you had down stream receptacles with more distance between there might still be some protection but maybe not as near the same level of protection because of the distance between them.
When you plug in a surge power strip do you expect it to protect everything on the BC, all the way back to the pole it came from, and thus all BC's on that side of the center tap? They only protect the recepts of the surge strip.
 
When you plug in a surge power strip do you expect it to protect everything on the BC, all the way back to the pole it came from, and thus all BC's on that side of the center tap? They only protect the recepts of the surge strip.
I expect it to absorb surges at that point in the circuit. Just like a whole house panel absorbs surges at that point in the circuit. Further you get from the protective device the less effect it may have on where you are at. Now the whole house device at the service panel still pretty good at knocking off surges that come in on the service conductors and lessening those effects on everything downstream. If I had a surge power strip plugged into a duplex receptacle, I'd think it still offers some level of surge protection to the other receptacle of the duplex. All it usually is is MOV's between the H,N and G conductors and nothing that is in series with the supply conductors and load conductors. If it were in series how does it drain off the surge energy?
 