I was always tought to run a 20 amp circuit for both . In a rough wire whrre you don't know the dishwasher or disposal. Has anyone goten burned running a 15 amp circuit?
I was always tought to run a 20 amp circuit for both . In a rough wire whrre you don't know the dishwasher or disposal. Has anyone goten burned running a 15 amp circuit?
I have found it to be a violation of 210.23(A)(2) on occasion...
a large disposal being the culprit.
I can' see how a 15amp would work for DW AND Disposal on same circuit. I run dedicated 20 or 15 for DW and usually put GD on the small appliance/ counter top circuit. Never had a problem
I can' see how a 15amp would work for DW AND Disposal on same circuit. I run dedicated 20 or 15 for DW and usually put GD on the small appliance/ counter top circuit. Never had a problem
One way I wired them was to run a 12/2 home run to a receptacle box under the sink close to the DW, breaking the hot tab on a duplex, then run a 12/2 up to the GD switch, then plug in the GD to the switched side of the duplex, then pigtail the DW and run the cord through the hole for the drain tube and plug into the non switched side
You should look at the manufacturers instructions and see what they recommend. Whatever they recemmend is required if it is a UL listed peice of equipment. The following excerpt came from REPORT ON DISCUSSIONS DURING UL MEETINGS WITH ELECTRICAL INSPECTORS AT THE 2007 IAEI SECTION MEETINGS
Following manufacturer?s installation instructions.
Question
AHJs are some times placed in a difficult position due to manufacturer?s installation instructions that are more stringent than minimum NEC? requirements. For a hot tub rated 50A, the installation instructions indicate that all supply conductors should be 6 AWG. The installer used an NM cable with a 10 AWG equipment grounding conductor. This would be a code-compliant installation, but had to be rejected by the AHJ because the instructions were not followed.
Answer
Installation instructions provided with UL Listed products are reviewed as part of the Listing investigation. Manufacturer?s recommendations that are part of the installation instructions should be followed in order to comply with NEC? Section 110.3(B). The AHJ should expect all installation instructions provided with UL Listed equipment to be available for review at the time of inspection.
this is the situation the rough wire home owners says they want a dishwasher and a disposal that they havent picked yet. id like to run them as seperate circuits I usally run a 12-3 and have 2 20 amp circuits im trying to save a buck so id like to run a 14-3 and have 2-15 amp lines.Is it likely ill need a 20 amp circuit for dishwasher or disposal?
It is amazing that the NEC sees a #10 as acceptable but the manufacturers of hot tubs are wanting a full size EGC. It irks me.