Commercial location (Greenhouse Growth lighting)
277V 30 amp lighting branch circuit
~660 watt LED ballasts
Looking at specifying l7-15p cord and plug connected (twistlock) 15 amp receptacles
For example a duplex Leviton 4750
So are these 15 amp receptacles legal for LED ballasts in recent code versions?
410.62 (C) 2 and 3 both allow "Inlets and connectors shall be permitted to be of a lower ampere rating than the branch circuit but not less than 125 of the luminaire load current." C.2 specifically allows branch circuits to 50 amps. Interesting that C.3 doesn't mention the branch circuit size...
660 watts/ 277V*1.25 = ~3 amps so that works for a 15 amp receptacle.
The problem is that neither 2 (Provided with Mogul-base, Screw Shell Lampholders) or 3 (Equipped with Flanged Surface Inlet) seem to apply to a remote LED ballast that is cord connected to a light engine.
I'm not sure what "Equipped with Flanged Surface Inlet" is referring to for a lighting fixture. Examples?
An example of the high wattage cord connected LED lighting fixtures in the use case:
My take is that #2 covers a 1000w HPS HID (remote) ballast, which is a very similar application. But maybe the code hasn't caught up to LED's yet?
Now if the 277V lighting branch circuit drops to 20 amps, I'm pretty sure there aren't any code issues with those receptacles, as 15 or 20 amp receptacles can be used on any (most?) 20 amp circuit.
Thanks,
Gregg Short P.E.
Greenhouse Design LLC
Burbank, OH
Commercial location (Greenhouse Growth lighting)
277V 30 amp lighting branch circuit
~660 watt LED ballasts
Looking at specifying l7-15p cord and plug connected (twistlock) 15 amp receptacles
For example a duplex Leviton 4750
4750
www.leviton.com
So are these 15 amp receptacles legal for LED ballasts in recent code versions?
410.62 (C) 2 and 3 both allow "Inlets and connectors shall be permitted to be of a lower ampere rating than the branch circuit but not less than 125 of the luminaire load current." C.2 specifically allows branch circuits to 50 amps. Interesting that C.3 doesn't mention the branch circuit size...
660 watts/ 277V*1.25 = ~3 amps so that works for a 15 amp receptacle.
The problem is that neither 2 (Provided with Mogul-base, Screw Shell Lampholders) or 3 (Equipped with Flanged Surface Inlet) seem to apply to a remote LED ballast that is cord connected to a light engine.
I'm not sure what "Equipped with Flanged Surface Inlet" is referring to for a lighting fixture. Examples?
An example of the high wattage cord connected LED lighting fixtures in the use case:
VYPR Series
Built for year-round production, the Fluence VYPR Series empowers the growers to have predictable production despite the season.
fluence.science
My take is that #2 covers a 1000w HPS HID (remote) ballast, which is a very similar application. But maybe the code hasn't caught up to LED's yet?
Now if the 277V lighting branch circuit drops to 20 amps, I'm pretty sure there aren't any code issues with those receptacles, as 15 or 20 amp receptacles can be used on any (most?) 20 amp circuit.