S ssadvis Member Apr 8, 2008 #1 Dose the Nec allow for 15 amp recepticles on a 20 amp branch circuit in a commercial building? I did the table 210.21 it seems to indicate that you can. Thanks
Dose the Nec allow for 15 amp recepticles on a 20 amp branch circuit in a commercial building? I did the table 210.21 it seems to indicate that you can. Thanks
iwire Moderator Staff member Location Massachusetts Apr 8, 2008 #2 Sure as long as there is more then one receptacle on the circuit.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Apr 8, 2008 #3 which also takes you back to this thread: http://forums.mikeholt.com/showthread.php?t=98050