bradleymattlin
Member
- Location
- Airville, PA
I have a question with a 15 hp air compressor. 208 voltage 3 phase. the full load current is 46.2. so for wire size i take it by 125 percent for 57 amps. i can run number 6 thwn/thhn. But for the breaker size i use 250 percent for the inverse time breaker and come up with 115 amps for breaker size. But the maunfacter told me i can put it on a 90 amp breaker and was trying to figure out why is this.