I don't deal with over 600v often enough to be half knowledgeable so I could use some verification here.
In have a customer owned arrangement with a 4350 KVA 12.4KV/575V 3 phase transformer.
Primary protection is 300 amp fusing. Primary wiring is muticonductor cable mv105 in cable tray transitioning to conduit. Termination ratings are unknown, possibly 90?.
E/C has elected to use 4/0 Cu cable. Based on 310.60(C)(73) {'11 Code}, I see no problem.
Am I overlooking something ?