15 kva isolation transformer grounding
15 kva isolation transformer grounding
Just snap a photo of the file and post it that way.
uested, as I have not received any responses to my questions posted in my sketch above. The one image shows the ACME spec sheet for the Xfmr that is actually being installed. It does not appear that the Xfmr is corner grounded. It appears that the Xfmr core is bonded to the case though. I'm assuming that the Xfmr case is grounded.
Question#1- Can i run a #10 equipment ground from the 277/480 Panel that is feeding the primary of the Xfmr, and bond the Xfmr case, and continue that ground to the 240 volt, 3 phase panel and Bond that panel as well? The 240 volt, 3 phase panel is for two- 3 pole 20 amp breakers that are feeding 2- VFD,s. No neutrals being used.
Question#2- Am I required to run a GEC from the Xfmr case to building steel? If so, can I run the GEC from the 240 volt, 3 phase panel to building steel instead?
Question#3- would I need to install phase monitor lamps that would alert me that 1 of the phases have grounded, which would then allow me to repair the first fault before a second fault occurred, as the the first fault would not trip the OCPD?
Question#4- Should I just bond the XO terminal of the Xfmr to the case instead of the above option, deriving the neutral and having a high leg at the 240 volt, 3 phase panel instead? This would seem to now require a bonding jumper and a supply side bonding jumper if I do it this way. I am hearing that this option may be safer.
Thanks to all. I want to insure that I am installing this correctly.