150 watt hps

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
I am not sure all HID caps are for PF correction.

Yup, caps across the incoming line will work. 55uF at something like 370 volts will work. Just make sure they are rated for HID fixtures.

I don't recall seeing a capacitor in an HID fixture that was connected line to line ahead of the ballast.

They always seem to be in series between the ballast and the lamp.

Metal_halide_ballast_wiring.jpg


Or on its own winding.


ld3ai_ld4p-2.GIF
 

kwired

Electron manager
Location
NE Nebraska
I am not sure all HID caps are for PF correction.



I don't recall seeing a capacitor in an HID fixture that was connected line to line ahead of the ballast.

They always seem to be in series between the ballast and the lamp.

Metal_halide_ballast_wiring.jpg


Or on its own winding.


ld3ai_ld4p-2.GIF
I don't believe the primary function of the capacitor when in series with the lamp is PF correction either, but I also think it still does improve PF to some degree. Seems like all luminaires with a capacitor in them have fairly high power factor.

Same for a PSC motor where the capacitor is in series with a winding, they usually have higher PF then a similar size motor that doesn't have a capacitor. The primary function in such a motor is phase shift to develop torque - not sure what the function of the capacitor in series with the HID lamp is though.
 

domnic

Senior Member
Occupation
Electrical Contractor
150 HPS

150 HPS

If i had 10 150 hps tights with 50% PF with on cap the line amps would be 32 amps if i had a cap the at each light the line amps would be 16 amps?
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I am not sure all HID caps are for PF correction.



I don't recall seeing a capacitor in an HID fixture that was connected line to line ahead of the ballast.

They always seem to be in series between the ballast and the lamp.

Metal_halide_ballast_wiring.jpg


Or on its own winding.


ld3ai_ld4p-2.GIF


Jeez, am I talking to actual electricians? :blink::slaphead:


That's because your showing a CWA ballast followed by a magnetic regulator. CWA, CWI and Regulated lag (3 core ballasts) all use the capacitor as a method of regulating lamp wattage and limiting arc current in addition to power factor correction (one reason the slightly off term constant wattage applies to them). Plus the advantage of lower starting current vs running current. R-HPF and HX-HPF ballasts on the other hand only use them for PF correction and can functionally operate without them. Yes, caps are connected line to line, or line to auto transformer tap for multi-tap ballasts so each voltage doesn't need a different cap.

The ballasts in question are pure inductors or inductor auto transformer types (reactor and reactor auto-transformer) which do not use a capacitor for lamp regulation. If they did and ran without a cap they would have failed thus far.

Reactor and HX-NPF all have the option of a cap connected before the ballast line-line. These ballasts make up 90% of low wattage 150 and below high power factor lighting fixtures. Just because you have never seen a high power factor reactor or HX ballast doesn't mean they doesn't exist.
 
Last edited:

iwire

Moderator
Staff member
Location
Massachusetts
Jeez, am I talking to actual electricians? :blink::slaphead:


That's because your showing a CWA ballast followed by a magnetic regulator. CWA, CWI and Regulated lag (3 core ballasts) all use the capacitor as a method of regulating lamp wattage and limiting arc current in addition to power factor correction


Jeez, am I talking to someone who can follow a thread? :blink::slaphead:


I will try to 'splain it to ya. :p

I jumped in when I read this exchange.

Lots I don't know either. I did not know that that the cap in HID a fixture was for power factor correction. Did you?

Nope. I just wired it up, never thought why.

It seemed to me that Dave and jumper had jumped to the conclusion that caps in HIDs were only for power factor correction. I felt that might be incorrect.

I offered up some examples in my first post of what I had worked with and did not believe the caps in those examples where for PF correction.

After that post I kept looking for more info and finding the document I posted showing what you were talking about. While I have worked with many of those ballasts the caps were absent.




Just because you have never seen a high power factor reactor or HX ballast doesn't mean they doesn't exist.

Never said that, I even posted a cut sheet with diagram showing one.

My point was simply that I have not been finding line to line connected capacitors in those ballasts in the real world. That being the case I doubt Dave or Jumper have been working with them either.


Capeesh? ;)
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Jeez, am I talking to someone who can follow a thread?


I will try to 'splain it to ya.

I jumped in when I read this exchange.





It seemed to me that Dave and jumper had jumped to the conclusion that caps in HIDs were only for power factor correction. I felt that might be incorrect.

I offered up some examples in my first post of what I had worked with and did not believe the caps in those examples where for PF correction.

After that post I kept looking for more info and finding the document I posted showing what you were talking about. While I have worked with many of those ballasts the caps were absent.






Never said that, I even posted a cut sheet with diagram showing one.

My point was simply that I have not been finding line to line connected capacitors in those ballasts in the real world. That being the case I doubt Dave or Jumper have been working with them either.


Capeesh?

Ok good enough:D:lol::p I thought you were referring only to my comment... sorry for the misunderstanding! :ashamed1::)
 

jumper

Senior Member
My point was simply that I have not been finding line to line connected capacitors in those ballasts in the real world. That being the case I doubt Dave or Jumper have been working with them either.

Ain't seen, worked, or ever heard (til now) of one.

Cap has always been inline between ballast and lamp like diagram#1 you posted.
 

kwired

Electron manager
Location
NE Nebraska
I can't recall ever seeing a ballast not inline with lamp either, didn't really know what it's purpose was being in line, but did figure it still had some impact on power factor as well.
 