150a service changed to 200a
Up grading 150a to 200a service,this in a garage ,two story home with finished walls.I know i have to also up grade to no. 4 to water pipe. Without tearing into walls to get to water pipe,my question is can the no.4 go out to ground rod and continue to crawl space to water pipe.Would this be code compliant,would this cover grounding reguirements on this part of up grade.
Dennis, are you sure? 250.68(C)-2011 seems to say no to this install. Am I misreading it?
I was assuming the connection was continuous since the op didn't mention cutting it. I also don't think this is an issue with compliance before the 2011. BTW, I have never done it that way.
I also think that section is saying if you use the water pipe as a bonding jumper you must connect the jumpers within 5'. Perhaps I am wrong.
Either way goodnight and Happy New Year.
Agreed.
The 5 feet mentioned is the first 5 feet of the water pipe after it enters the building or structure - the part that is considered a part of the electrode.
You could connect your CEE, ground rod, other electrodes to the first 5 feet of water piping instead of to your service equipment if you want to, is all it is saying.
I agree and I thought that was what I was saying. The bonding jumpers from the water pipe must be connected to the first 5 feet of pipe. In the past I believe you could use any part of the piping as a bonding jumper.
You said within 5 feet but did not mention from the entrance to the building, I thought that needed some clarification