What awg conductor would you recommend for a 150amp sub-panel, that is 110ft distance from the 400amp main panel? What size for the 3 conductors and what size for the ground?
It is a conduit run, copper conductors. 120/240 single phase. 150amp sub-panel supplying lighting, general outlets, HVAC w/ heat pump in a studio.
You say I need 1/0 with #6 ground. I was thinking #1 with #6 ground.
Please comment. thanks.
Most likely 130 amps will run the studio fine, but I don't know for sure. The heat pump condenser requires a 45amp breaker, the air handler w/ the 15kw heat strip requires a 30amp and a 60amp breaker. The rest of the studio is just lights, refrig, computers, makeup area with normal hairdryer. 1800 sq.ft studio.
How many amps would you guess it will pull?