15A AFCI/GFCI SELF-TEST TR REC WHT

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I believe to do so would require a metallic wiring method from the supply to the device {210.12(A)(5)}
 
Last edited:

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
I believe to do so would require a metallic wiring method from the supply to the device
Augie refers to 210.12(A)(5) where adopted for new work, but there are other methods.

* Old Work Method - 406.4(D)3&4 replacement code allows breakers, or AF/GF Outlets at first opening, regardless of existing-wiring method.

* Universal Method - CAFCI breaker w/ GFCI outlet at first opening. Works for all work & wiring methods.
Only method available before Dual Function breakers / outlets existed.

* Numb Nutz Method - No AFCI at all, and GFCI reset buttons on every outlet, or other than first outlet.
Found in > 90% of all tenements after 1st remodel. Passes inspection in all States w/ Numb Nutz combination / General / code-enforcement inspectors

* Chamber of Commerce Method - Lobby legislators to amend out AFCI's, and De-fund AHJ's with dedicated-electrical inspectors.
Building Associations want laborers to rip Romex without AFCI's, and are forcing all inspectors to pass Numb Nutz Method in several States.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I agree with Fred (if this is a new circuit and the breaker is a standard non GFCI/AFCI)
 

jap

Senior Member
Occupation
Electrician
so that receptacle is only intended for remodels and circuits run in EMT
The intent of the receptacle has nothing to do with it.

It's about Arc Fault protection of the circuit conductors.

You had asked if that device could be used "at the first outlet" instead of using a breaker as the circuit conductor protection.

Where Arc Fault protection is required, It could be used "at the first outlet" if the proper wiring method such as EMT or other approved methods are used to protect the circuit conductors between that first outlet and its origin at the (breaker panel) simply put.

EMT or other approved methods greatly reduces the chances of the circuit conductors being penetrated by a nail, screw, etc... that may cause a an arcing fault.

If you do not use a proper wiring method such as EMT or other approved wiring methods to reduce the chance of the circuit conductors being damaged,then no, you can't install it at the first outlet since the wiring ahead of the first outlet would not be Arc Fault protected properly.

Or so they say.

JAP>
 