I think it is well established that the Code permits a single 15A duplex receptacle to be installed on an individual branch circuit (say, one run of 12/2 Romex). Article 210.21(B)(3) is the section that permits this - see "Is it legal to install a 15A receptacle on a 20A circuit?" in this forum for more info.
My question is this: does the Code permit a single 15A duplex receptacle to be installed on a 20A multiwire branch circuit (say, one run of 12/3 Romex - in this case, you would break the tab on the hot side of the duplex but not on the neutral side.)
*My feeling* is that the answer rests on whether you define a multiwire branch circuit to be one (1) circuit or two (2) circuits. Article 210.4(A) "Multiwire Branch Circuits" > "General" states that a MWBC is "...permitted to be considered as multiple circuits." Additional Code language refers to a MWBC as a singular "branch circuit" (i.e. 210.4(B)). This indicates by inference that normally a MWBC would be considered a single circuit. If this is true, then 210.21(B)(3) would allow the 15A duplex to be installed on this circuit.
The background info is below, but I'd rather just answer the question based on pure Code alone for the simple case posed above.
The MWBC and duplex receptacle are for cord & plug connected dishwasher and garbage disposal. The hot leg for the disposal's portion of the duplex receptacle is also switched. Inspectors from certain municipalities are not allowing the 15A duplex for this type of installation, requiring a 20A duplex instead. I believe their rationale is that the MWBC is two circuits and therefore the 15A duplex is split into 2 receptacles with only one installed on each circuit.
My question is this: does the Code permit a single 15A duplex receptacle to be installed on a 20A multiwire branch circuit (say, one run of 12/3 Romex - in this case, you would break the tab on the hot side of the duplex but not on the neutral side.)
*My feeling* is that the answer rests on whether you define a multiwire branch circuit to be one (1) circuit or two (2) circuits. Article 210.4(A) "Multiwire Branch Circuits" > "General" states that a MWBC is "...permitted to be considered as multiple circuits." Additional Code language refers to a MWBC as a singular "branch circuit" (i.e. 210.4(B)). This indicates by inference that normally a MWBC would be considered a single circuit. If this is true, then 210.21(B)(3) would allow the 15A duplex to be installed on this circuit.
The background info is below, but I'd rather just answer the question based on pure Code alone for the simple case posed above.
The MWBC and duplex receptacle are for cord & plug connected dishwasher and garbage disposal. The hot leg for the disposal's portion of the duplex receptacle is also switched. Inspectors from certain municipalities are not allowing the 15A duplex for this type of installation, requiring a 20A duplex instead. I believe their rationale is that the MWBC is two circuits and therefore the 15A duplex is split into 2 receptacles with only one installed on each circuit.