Can 15A light switches be used on 20A circuits?
(assume lighting load is less than 15A)
Can 15A light switches be used on 20A circuits?
(assume lighting load is less than 15A)
Switch as opposed to receptacle.
Can someone point me to the relevant NEC paragraph?
Switch as opposed to receptacle.
Can someone point me to the relevant NEC paragraph?
404.14 specifies the load that can be connected to the switch, not the rating (current protection) of the branch circuit that the switch is connected to. (unless I am missing something which could be the case.)
This is driving me nuts. It seems normal but I can't find anything to say it is.
Perhaps the 15A switch is listed for 20A circuits by the manufacturer?
404.14 specifies the load that can be connected to the switch, not the rating (current protection) of the branch circuit that the switch is connected to. (unless I am missing something which could be the case.)
I believe 404.14 covers it.