I'm working on adding a few outlets on the side of my house and backyard and had a quick question. I ran a 12awg wire home run from a 20amp breaker on my sub panel to a 20amp GFCI. I connected the load terminals to a 15amp outlet and plan to continue on to a few more 15amp outlets from there. Do you see any issues with this? I wasn't sure if the outlets would have to be rated for 20amp.

Thanks in advance!
 
License may not be needed if working on his own home - permits however may be needed.
True but we are not allowed to help diyers. I know in California that some general contractors are allowed to do some electrical work--OP is a GC
 
Hi all,

I'm working on adding a few outlets on the side of my house and backyard and had a quick question. I ran a 12awg wire home run from a 20amp breaker on my sub panel to a 20amp GFCI. I connected the load terminals to a 15amp outlet and plan to continue on to a few more 15amp outlets from there. Do you see any issues with this? I wasn't sure if the outlets would have to be rated for 20amp.

Thanks in advance!

Don't drop the wire size to the rest of the circuit containing the 15 amp receptacle outlets. Stay with the #12.
 