Is it ok to have 15A switches on 20A circuits and if so, where is this stated in the NEC?
mshields Senior Member Location Boston, MA May 25, 2017 #1 Is it ok to have 15A switches on 20A circuits and if so, where is this stated in the NEC?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician May 25, 2017 #2 Yes it's permitted although it's not directly stated in the NEC. If you think in terms of incandescent dimmers some have a maximum load of 600 watts which if they were sized for the branch circuit you would need a 5 amp OCPD.
Yes it's permitted although it's not directly stated in the NEC. If you think in terms of incandescent dimmers some have a maximum load of 600 watts which if they were sized for the branch circuit you would need a 5 amp OCPD.
luckylerado Senior Member Location Lake of the Ozarks May 25, 2017 #3 mshields said: Is it ok to have 15A switches on 20A circuits and if so, where is this stated in the NEC? Click to expand... It is dependent on the type and size of the load and the type of switch being used. See 404.14
mshields said: Is it ok to have 15A switches on 20A circuits and if so, where is this stated in the NEC? Click to expand... It is dependent on the type and size of the load and the type of switch being used. See 404.14