Thjs was in another thread that already had way too many twists and turns, but I did want to bring it up, so I broought it here:
If it was answered, it didn't make the original quote, but I'd like to understand the answer to the switch part of the question:
I understand that all UL listed receptacles are actually investigated for use in 20a circuits, and that 15 and 20a versions of any given grade actually use the same internals, differing only in slot configuration. That all makes sense.
What I don't understand is why a 15a rated switch can be used to switch a 20a circuit.
Necdigest ?, February 2007
Compiled by Jeff Sargent and the NFPA Electrical Engineering Team
Q. Can I use 14-2 wire for the switch leg of a light fixture where the branch circuit is protected by a 20-amp circuit breaker? If this is against Code, why can I use 15-amp switches and receptacles on 20-ampere circuits?
A. The conductors from a switch location to the lighting outlet it controls are considered branch circuit conductors, not tap conductors connected to branch circuit conductors. These conductors are subject to the general overcurrent protection requirements of Section 210.20(B), which points to Section 240.4 for the specific overcurrent protection requirement. Section 240.4(D) specifies that 14 AWG copper conductors are to be protected by an overcurrent protective device with a rating or setting no higher than 15 amperes. And Table 210.24, which summarizes the requirements for branch circuits with two or more outlets or receptacles, specifies that the minimum conductor size for a 20-ampere-rated branch circuit is 12 AWG......
If it was answered, it didn't make the original quote, but I'd like to understand the answer to the switch part of the question:
If this is against Code, why can I use 15-amp switches and receptacles on 20-ampere circuits?
I understand that all UL listed receptacles are actually investigated for use in 20a circuits, and that 15 and 20a versions of any given grade actually use the same internals, differing only in slot configuration. That all makes sense.
What I don't understand is why a 15a rated switch can be used to switch a 20a circuit.