Possibly a #12...maybe even a 14.

Looking at T430.149 , a 15Hp motor @ 460v is 18A.


Is there more to the question? Duty cycle, etc..
 
Not enough information.
-3 ph or 1 PH?
-As Celtic ask, duty cycle.............?
-What is this motor being used for?
-Is a fire pump involved?
 
Celtic,
Looking at T430.149 , a 15Hp motor @ 460v is 18A.
That would be a rare motor...that table is for two phase 4 wire motors, however if you did have that motor the code would not permit the use of #14 unless the terminations and equipment were listed for use at 90?C. 1.25 x 18 = 22.5A.
Don
 
The point of my answer is that is not enough information was given.

We can speculate as to what the OP is actually asking...but we won't know for sure until he offers more.

celtic said:
The output is only as accurate as the input. :wink:
 
I've done shot a flair, I've learned the Code Wrong!

I've done shot a flair, I've learned the Code Wrong!

trallio said:
What is the minimum size conductors which can be used to feed a 15hp, 460V motor?

celtic said:
Looking at T430.149 , a 15Hp motor @ 460v is 18A.

Now Im using 2005 -NFPA.
Now I'm trying to play along here at home, I ususally go right to the stated article(s). where's 430.149 - table article or other.????
Maybe its 430.249! ?

If one starts in the beginning of article 430, 430.149 isn't listed in Figure 430.1 Article 430 Contents. Theres no grey shading in Fig. 430.1 in 2008. Back to the question and based on Figure 430.1, Motor circuit conductors lies with 430.21 through 430.29.

Now I know where all in various degrees of Code applications in the forum, I just wish the questioner/OP would state where they are in respect to there code cycle. Theres very little grey up to the point of, you guessed it 430.126- 08'

This all tells me two things about the way people solve or answer a problem here. They do it based on learned behavior including the part I've done it this way forever, and negate what is being asked. Or they do it this way based on researching the answer based on the quantity or value of the question, as said theres not enough information!

I really need to get out more if you guys are hooking up 480 Two-Phase
Alternating-Current Motors (4-Wire).:grin:
 
Sorry.

The '02 NECH just looks so much nicer than the '05 NEC.:roll:

I've really got to start (at the very least) referencing the edition NJ uses: '05.

T430149.jpg


T430249.jpg



Both tables are the same with the exception of the table number.


Good catch!
 
cadpoint said:
I really need to get out more if you guys are hooking up 480 Two-Phase
Alternating-Current Motors (4-Wire).:grin:

The two-phase motors are all the rage.......someplace :grin:
 
More info

More info

The motor will be a standard 460V, 3ph
It is for a fan in some HVAC equipment at a power plant.
There is no magic to this thing that I know of except that some PLC programmer who is technically an electrical engineer is claiming that #12's are enough. As he is a customer, we agreed to "investigate" but told him that we believed that #10's are the proper size for a 15hp motor- especially in an industrial envrionment.

The one modifier is that the distance is in excess of 300'. But I didn't want to confuse voltage drop with the heart of the question.