15HP motor on panel

Status
Not open for further replies.

la2151

Member
Location
california
HI.. am looking for others thoughts on putting that large of a air compressor motor on a existing panel that is all used for general office lights & plugs? I don't like the idea & my electrical engineer recommends I not do it.. The GC keeps asking why not too :) dsnt totally believe me..
Thanks for input guys.
 

la2151

Member
Location
california
motor on panel.

motor on panel.

sorry wasn't thinking. gave a really broad description. It is a 120/208 3 ph 200 amp panel. the existing load is only 90 amps. the new 15hp motor is 208 3 ph as well. I am more worried about lights dimming every time the air compressor comes on. MY electrical engineer calctd it as ok but he expressed a concern on motor starting.. It is just the GC that is saying are you sure??? GC can be stubborn. what are others thoughts. I think the feeders to panel are at least 3/0.. have to ck on monday
thanks
 
Well its important to determine what size the breaker is feeding this panel. 3/0 conductors are good for 200 amps so I am assuming that the breaker is sized for 200A. If this is the case then it shouldnt be an issue, 15hp motors at 208V 3ph account for 46.2 FLA. Breakers for motors are typically sized for 1.75 of the FLA to account for initial startup. 90A + 46.2A X 1.75 = 170.85A so you should be ok.
 