Have a lot of 1/c #4/0 15kv cable CU that they want us to VE to AL. How would I approach this to account for the correct AL size cable? Thanks.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
At first you have to state a few details:
-current [normal, short-circuit]
-cable route [for instance: underground, conduit, duct, RHO, ambient temperature]
-how many cables per conduit or duct or tray or else.
 

Ingenieur

Senior Member
Location
Earth
wag
you want the same cable type, insul, etc
in Al with an ampacity equal to Cu 4/0 unless the Cu is oversized, then base on load i

it may impact conduit size
you could also look at C, L and R for equivilence
 