M mstrlucky74 Senior Member Location NJ Jul 10, 2018 #1 Have a lot of 1/c #4/0 15kv cable CU that they want us to VE to AL. How would I approach this to account for the correct AL size cable? Thanks.
Have a lot of 1/c #4/0 15kv cable CU that they want us to VE to AL. How would I approach this to account for the correct AL size cable? Thanks.
Julius Right Senior Member Occupation Electrical Engineer Power Station Physical Design Retired Jul 13, 2018 #2 At first you have to state a few details: -current [normal, short-circuit] -cable route [for instance: underground, conduit, duct, RHO, ambient temperature] -how many cables per conduit or duct or tray or else.
At first you have to state a few details: -current [normal, short-circuit] -cable route [for instance: underground, conduit, duct, RHO, ambient temperature] -how many cables per conduit or duct or tray or else.
I Ingenieur Senior Member Location Earth Jul 13, 2018 #3 wag you want the same cable type, insul, etc in Al with an ampacity equal to Cu 4/0 unless the Cu is oversized, then base on load i it may impact conduit size you could also look at C, L and R for equivilence Last edited: Jul 13, 2018
wag you want the same cable type, insul, etc in Al with an ampacity equal to Cu 4/0 unless the Cu is oversized, then base on load i it may impact conduit size you could also look at C, L and R for equivilence