Is this an excitation transformer connected directly to the generator terminals? (300V secondary is a typical excitation system supply voltage.)
If that?s the case, the excitation transformer is usually included in the generator's differential protection zone. A fault in the excitation transformer is detected by the differential relays that trip the generator and the generator breaker, removing power from the transformer. The transformer is typically small enough compared to the generator rating that separate CT?s aren?t even required on the transformer. This is for short circuit protection, not OCP.
Sometimes, the excitation transformer is considered part of the generator supplier?s system with inherent overload protection.
One way of adding OCP is putting CT's on the cables feeding the transformer or on the transformer HV bushings. Connect the CT's to an overcurrent relay that trips the generator and generator breaker. This is cheaper and more reliable than a fused switch or circuit breaker.
IMO, it might be possible to use the tap rule and not have individual OCP. The generator overcurrent protection would have to be set for less than 400% of 400 kVA (1600 KVA) (NEC 240.21 (B)(3). Also, the generator should not be capable of paralleling with the utility otherwise there would be two sources of power to the transformer: generator and utility.
The 240.21 requirements for secondary conductors also need to be considered.