I'm trying to confirm the ampacity/design intent of an existing installation. It consists of 4x 15kV copper MV-105 500 mcm /phase in tray with more than 1 cable diameter spacing between cables, single layer. It's an outdoor ladder tray. It has a ventilated cover which is where I'm getting stuck. 392.80.B.2 only discusses uncovered tray or solid covered tray, neither of which seem to apply here. I'm thinking, based on the cable spacing, whoever designed it was going for the 392.80.B.2 (2) requirements which do not require a derate, but that language specifically says "uncovered". To me, a ventilated cover is not uncovered.
Other elements in the circuit (bushings, breaker) are rated for 3000A but I'm not sure this cable installation meets that rating.
Looking for some feedback here. Thanks!