15kVA Single Phase Secondary OCPD size
Sparky2791
Northeast, PA
Electrical Design
Per the National Electric Code, can a 15kVA stepdown transfomer feed a 100A panel (208V single phase secondary)
15000/208 = 90.14423A which is over 90A and the next standard OCPD is 100A. While I would recommend the use of a 20kVA would a 15 be acceptable?
Thanks for the replies!
A transformer can feed any load you want. The NEC is worried about too much overcurrent protection, not too little. The requirement is that the secondary protection does not exceed 125% of the transformer output only if the primary side protection is also above 125%.
So what is your primary OCPD size?
Pretty sure your math is incorrect. 15,000 / 208 = 72 amps (not ~90 amps). Im assuming you mean (15,000 / 208) x 1.25 = ~90A.
Keep in mind that transformers come in standard sizes. It may be difficult to find a readily available single-phase dry-type transformer in a 480v primary / 208v secondary arrangement. Similarly, a 20kVA single phase transformer isn't a standard size. It goes 15kVA to 25kVA (most with 240v secondary).
Let me clear this up, sorry I typed it quickly.
Primary is 480V single phase
Secondary is 120/208V single phase
Yes (Npstewart) my OP forgot to show the 125% in my math and the next standard size single phase transformer size would be a 25kVA.
Since the following calculation gets me over 90A (90.14423A) can maximum secondary OCPD be 100A (next standard size).
15000/208 = 72.115384A x 125% = 90.14423A (100A OCPD permitted?)
That is an impossible specification.
120/208V 'single phase' is actually 2 legs of a 3 phase system (I propose that we call it 'psingle phase'...) You _can't_ get it from a single phase transformer. (You could in theory have a 208V single phase coil with a 120V tap, but that would put 88V on the other leg and it wouldn't be close to standard 120/208V.)
I suspect that you are looking for a 480: 120/240V single phase transformer, or a 480 : 208/120V three phase transformer.
If you actually have a 15 kVA 208V transformer, then you can use the 'next size up' rule for the secondary _transformer_ protection. But the 'next size up' rule doesn't apply to the secondary conductors. (I think....) So you would need 100A _conductors_ if you use a 100A OCPD.
In theory I suppose one could make a two core open delta primary / open wye secondary that used two primary legs and a neutral, then you could get 120/208 open wye.
Agreed, but calling a transformer bank with two separate cores connected to the three primary phases a single phase transformer is even more of a stretch than calling '120/208V 3 wire' single phase :)
Yikes! You are all correct! Tunnel vision on this one and so sorry to confuse. 120/240V is secondary voltage, so my math is all off.
Will need a 25kVA to feed a 120/240V single phase 100A MCB panel.
Sorry folks mostly deal with 120/208V three phase WYE. So the 208V over road the 240V reference!
Apologies for wasting everyone's time!
Yeah agreed the terminology used to describe open wye needs improvement, the NEC refers to is as single phase in at least one place Article 310.12 formerly 310.15(B)(7) in the 2017:
"single-phase feeder conductors consisting of 2 ungrounded conductors and the neutral conductor from a 208Y/120 volt system"
I personally think adding a definition of 'open wye' to the NEC would be an improvement as none of the current NEC descriptions even cover a true open wye system doing a quick search I see it described a few different ways;
"a 3-wire circuit consisting of two phase conductors and the neutral conductor of a 4-wire, 3-phase, wye-connected system"
In a least three places; Article 310.15 (E)(2) formerly 310.15(B)(5)(b) in the 2017, 400.5(A) and 520.44
then described as
"a 3-wire circuit consisting of 2 ungrounded conductors and the neutral conductor of a 4-wire, 3-phase, wye-connected system"
In 220.61(C).
if the code defined open wye (and open delta for that matter) it would clear up some confusion and add some consistency.
I would calculate open wye like 'single phase' and its typically only used to power single phase residential loads but since it gets special treatment in several articles it should have a definition.
Well it was a good thought experiment.