I’m wiring a15kw heat pump. It has (2) 60amp pre installed breakers in the unit already. The load on the unit at 240v is 62.5 amps. The hvac guy said it’s 80amp electric heat with a 30amp outside unit. Which makes sense when you calculate 15kw at 240v and 1.25% correct? My first question is why the (2) separate 60amp breakers in the unit itself? Should I supply (2) separate feeds to these breakers and breaker them both at the correct size in the main panel at 70amps? Or should I run an 80amp feed to the unit? A little confusing
#1
Start with reading 424.22 (B). Over current protection.
48*1.25=60
Read carefully as you get to the lower half of B. Where the subdivided load is less.
#2 then read 424.22 (C). Over current devices.
Key word, supplementary and factory installed.
As you read second paragraph pay attention to the language in the first sentence.
Once you got that move to C. Now you can work on the branch circuit that feed the unit. You under 50 so stop reading. Branch circuit is a key word.
Now move to E.
The first paragraph is what you you need to size the branch circuit.
E applies since you have sub divided load. Do not skip the second sentence in E.
Now read name plate carefully as it may or may not be able to have two branch circuits feeding the unit.
Usually there is a sticker placed on the unit by HVAC if this is a field installed aux heat unit (s). 424.28
FYI. This is a standard test question for those who read. So high light 424.22.
Additional note as you read start off with part 3 article 424.19 then move forward. A applies since you have supplementary over current protection. Again key word: supplementary. So skip 424.19 B.
The key word branch circuit. See 424.3. (B).
When choosing the conductor insulation type see 424.11.
Some AHJ inspectors look for this.