So When sizing Conductors for 15kw heat with a 3.9A Blower motor.
You Have 15000/240=62.5A + 3.9A = 66.4A x 125%= 83A
Conductor is 83A = #4 Thhn
OCP is 83A so Code says if not a standard size fuse you need to go up to next standard size.(240.4B) 240.6A)
With all that said is it all right to run a #4THHN and install 90A Fuses.
Also I am running one feeder and using the tap rule to tap a #10 thhn for 5kw heat strip on 30A breaker in unit and #6 thhn for 10KW heat strip on 60A breaker in unit. I do not have room to install a panel and use branch circuits to unit and not comforable with the tap rules
Is this all code compliant
You Have 15000/240=62.5A + 3.9A = 66.4A x 125%= 83A
Conductor is 83A = #4 Thhn
OCP is 83A so Code says if not a standard size fuse you need to go up to next standard size.(240.4B) 240.6A)
With all that said is it all right to run a #4THHN and install 90A Fuses.
Also I am running one feeder and using the tap rule to tap a #10 thhn for 5kw heat strip on 30A breaker in unit and #6 thhn for 10KW heat strip on 60A breaker in unit. I do not have room to install a panel and use branch circuits to unit and not comforable with the tap rules
Is this all code compliant