I have been tasked with replacing two aged generators, combining them into two paralleled units. The load on these plus the new load we'll have means that we are going to be looking at about 1500kW worth of generation. It had been 1000kW until recently. And when it was, I was gravitating toward the Generac Gemini whose breakers on the output of each 500kW generator is 900A. I like this, because, it meant that I could feed the Emergency Generator Switchboard with two 900A breakers with all feeder breakers less than that.
I liked it because that meant I didn't need to have ground fault and that, in turn meant, that I wouldn't have to replace 16, 3 pole ATS's with 4 Pole ATS since ground fault protection at the generator won't work with 3 pole ATS's.
What I want to know is whether or not I am either over thinking this or thinking about incorrectly. I would welcome your input.
Thanks,
Mike
I liked it because that meant I didn't need to have ground fault and that, in turn meant, that I wouldn't have to replace 16, 3 pole ATS's with 4 Pole ATS since ground fault protection at the generator won't work with 3 pole ATS's.
What I want to know is whether or not I am either over thinking this or thinking about incorrectly. I would welcome your input.